You are only utilizing three wires, the supply system is still three phase four wire. No different from running a single two wire circuit @ 120 or 277 volts from a wye supply.4 wire up to the main, after that its technically 3 wire.
A three phase three wire "system" is typically a delta supply, can either be ungrounded or corner grounded.