On a typical service the grounded service conductor is connected by the bond jumper to provide a return path for ground faults.
I saw a 3 phase 3 wire service with no service conductors other than the 3 phase conductors.
3 service conductors in and 3 load conductors out from the service main breaker and a connection to an electrode system is all they have in the customers service. No others conductors were provided by the utility company.
Is this OK?
What acts as the ground fault return path to the source?
Are you sure one of the phases wasn't grounded? (corner grounded)