Which takes it to ground?
no the neutral would take it back to the transformer winding
Which takes it to ground?
That does not mean that dirt is part of the current's path. It means that the center point of the 120/208Y transformer secondary is intentionally connected to dirt. There are a number of good reasons for doing this, but giving current a path to planet Earth is not one of them.It's a grounded conductor.
It's a grounded conductor.
No. The neutral is. Grounded or otherwise.And I didn't say it was. Ground is a potential point at the transformer. The grounded CONDUCTOR is the best way to get there.
No. The neutral is. Grounded or otherwise.
But, as I already posted, the OP's question has been answered. Succinctly I was told.
Now, can we leave it at that? We don't want to confuse the issue, do we?
We are done. Move on.Not all grounded conductors are neutrals. But we usually refer to them as such for convenience.
We are done. Move on.
Only if a grounding electrode is installed and a grounding electrode conductor ties it to that point at the transformer.And I didn't say it was. Ground is a potential point at the transformer. The grounded CONDUCTOR is the best way to get there. This wasn't a thread about grounded conductors, but about pole current, hence the lack of detail. But I should have known better.
Ground.
The earth.
Only if a grounding electrode is installed and a grounding electrode conductor ties it to that point at the transformer.
Could a system without such have a neutral? I hadn't considered that.
Theoretically, yes, of course. You could, for example, have a transformer with multiple hot conductors and a neutral on the secondary and not ground any of them and it would work just fine. It might not be safe or legal but it would work. The neutral in a split phase system is merely the midpoint between the two phase voltages; it doesn't need to be grounded to act as the neutral.Could a system without such have a neutral? I hadn't considered that.
"Hot conductors" leads to some misunderstanding sometimes. What most people call "hot conductors" is generally referred to as "ungrounded" if using proper terminology.Theoretically, yes, of course. You could, for example, have a transformer with multiple hot conductors and a neutral on the secondary and not ground any of them and it would work just fine. It might not be safe or legal but it would work. The neutral in a split phase system is merely the midpoint between the two phase voltages; it doesn't need to be grounded to act as the neutral.
Grounding provides a voltage reference to ground but usually no current flows into (or out of) it.
"Hot conductors" leads to some misunderstanding sometimes. What most people call "hot conductors" is generally referred to as "ungrounded" if using proper terminology.
Many get confused with corner grounded systems and don't understand that you can ground a "phase conductor" - as I said before you can only ground one point of the system, NEC typically wants it to be whatever point leaves you with lowest potential to other points of the system, which a true neutral is equal to all other points of the system and will be lowest potential
Which is why I said "true neutral".I will only argue with your "lowest potential" term. A neutral will at any point in time have a potential which is lower than one phase conductor and equally higher than the other in a split phase system. Three phase gets a little more complicated.
Which is why I said "true neutral".
Neutral of a high leg delta isn't a true neutral to the entire system, and NEC never used to call this particular use a neutral until sometime in the last 10 -15 years.
Fair enough, I guess that lowest absolute value voltage of all the conductors is what I was trying to say.That's not what I was saying. In, for example, in a "normal" 1P3W service where the neutral is grounded, at any point of time other than a zero crossing, one phase is at a higher relative voltage (potential) than the neutral/ground and the other is at a lower (negative) voltage. The neutral does not have the lowest potential of all the conductors. If you were to say that a grounded neutral has the lowest absolute value voltage of all the conductors, I would agree with that.
I can relate to that.