3 phase boost set-up for tanning beds

Status
Not open for further replies.

phil

Member
Location
Kansas
Does anyone have some information on what rating an individual transformer would need to be when configured into a Auto-Wye connection from 208 to 230 in order to feed a 400 amp panelboard. Some of the conductor sizing on the engineers submitted diagram doesn't seem quite right. I read some information regarding this connection and they say it can handle much more than the rated kva. Haven't ran into this one before, any information would be helpful.
 
Re: 3 phase boost set-up for tanning beds

Based on the assumption that you a applying a 4w system wye-wye and the reference that I have you will need (3) 5kva 1ph B-B transformers with 120x240 pri -12/24 sec wired correctly as boost transformers. The transformer manufacturer should have a the correct transformer ordering information and wiring diagram available for you.
 
Re: 3 phase boost set-up for tanning beds

Phil
Buck boost transformers are only boosting a few KVA to raise the voltage so they will be many times lower then the rated load. Square D has allot of info on them at :

Square D buck/boost

Click on the calculator to figure what size you need.
 
Re: 3 phase boost set-up for tanning beds

I will try to explain what he meant.

Lets say the tan bed is 30 amps. at 230 volts that equals 30 x 230=6900 or 6.9 Kw.

But in this case of a boosting transformer we are only boosting the voltage 24 volts.

That same 6.9 Kw transformer is good for 288 amps. at 24 volts.So you size the Kw accoring to your boosting voltage which is 24 volts.

24x30=720 watts or .720 kw.
 
Re: 3 phase boost set-up for tanning beds

Thanks gentlemen, the explanations and information have helped tremendously.
 
Re: 3 phase boost set-up for tanning beds

Please be aware that if you are boosting a wye system that the neutral will also get boosted. Your 208Y/120 will become 230Y/133.
 
Re: 3 phase boost set-up for tanning beds

Originally posted by jim dungar:
Please be aware that if you are boosting a wye system that the neutral will also get boosted. Your 208Y/120 will become 230Y/133.
Jim, explain to me how the neutral gets boosted. :confused:

Rattus
 
Re: 3 phase boost set-up for tanning beds

Originally posted by jim dungar:
Vln = Vll/1.732
"

Jim, did you mean to say "line to neutral" instead of "neutral"?

Rattus

[ July 22, 2005, 12:22 PM: Message edited by: rattus ]
 
Re: 3 phase boost set-up for tanning beds

No, I meant neutral. Actually the voltage N-G may be different as well as the voltage L-N.

On a wye system the neutral point of a buck-boost transfomer may not be the same point as the original wye location. In these cases you can not bond the new neutral to ground.

If the transformer is derived by buck-boosting the original line-neutral voltage then the resulting neutral will be the same as the original. If the transformer is based on line-line voltages then the new neutral will be electrically different than the original. This is a major concern when supplying single phase loads buck-boosted from three phase wye systems.

Whish I knew how to post drawings.
For simplicity, assume a 280Y/120 transformer with normal X1, X2, X3, and X0 terminals and a boost transformer from 208 to 228.8V which will be a series connection of windings E, F, G, H, and K. X2 connects to F, X3 connects to H the load is connected to E and K. This leaves G as the center point (or neutral). What we now have is a right triangle XO to X2(F) is the hypotenuse at 120V, X2(F) to G is the vertical leg at 104V, and X0 to G is the horizontal leg at 60V.
 
Re: 3 phase boost set-up for tanning beds

Where is Ed with his collection of diagrams?

I think I see this, but a picture would be worth a lot of words. I think you have to post your diagram to your own website and provide a link to it.
 
Re: 3 phase boost set-up for tanning beds

With a 12 volt boosting voltage with Wye I came up with 228 volts Lines 1,2 and 3 and 132 neutral.

120 + 12=132 volts neutral

Phase voltages line to line 132x1.73=228 volts

Heres the one I had in mind

This diagram did not give the voltages my guess would be H=120 and x=12

[ July 22, 2005, 06:04 PM: Message edited by: ronaldrc ]
 
Re: 3 phase boost set-up for tanning beds

Yes, that is a connection, but note how they do not bond the new neutral.
 
Re: 3 phase boost set-up for tanning beds

Jim I don't understand what you mean,if you take that center tap to your Tan bed panel neutral bar and not ground to equipment you would have a neutral. But it would be a higher voltage.Or am I missing something here?

Ronald :)
 
Re: 3 phase boost set-up for tanning beds

Ronald, I think Jim is configuring a buck-boost xfrmr (2 cores)as an auto-xfrmr. The windings are connected as follows:

LV, HV, HV, LV

208V is applied to the HV windings, and the LV windings provide the boost to 230V.

There are two neutrals--a 3-phase neutral which is unchanged, and a single phase neutral which is 60V away from the 3-phase neutral (ground). This second neutral cannot be grounded. Two more buck-boosts could be connected in the same way, and the original 120/208 wye is still available.

Right Jim?

Rattus :p
 
Re: 3 phase boost set-up for tanning beds

Rattus now you have confused me. :) PS I'm showing a auto type wye

[ July 22, 2005, 06:41 PM: Message edited by: ronaldrc ]
 
Re: 3 phase boost set-up for tanning beds

This is a 120X240 to 12/24 schematic for 208-230v wye-wye.
208230.jpg
 