Re: 3 phase boost set-up for tanning beds
No, I meant neutral. Actually the voltage N-G may be different as well as the voltage L-N.
On a wye system the neutral point of a buck-boost transfomer may not be the same point as the original wye location. In these cases you can not bond the new neutral to ground.
If the transformer is derived by buck-boosting the original line-neutral voltage then the resulting neutral will be the same as the original. If the transformer is based on line-line voltages then the new neutral will be electrically different than the original. This is a major concern when supplying single phase loads buck-boosted from three phase wye systems.
Whish I knew how to post drawings.
For simplicity, assume a 280Y/120 transformer with normal X1, X2, X3, and X0 terminals and a boost transformer from 208 to 228.8V which will be a series connection of windings E, F, G, H, and K. X2 connects to F, X3 connects to H the load is connected to E and K. This leaves G as the center point (or neutral). What we now have is a right triangle XO to X2(F) is the hypotenuse at 120V, X2(F) to G is the vertical leg at 104V, and X0 to G is the horizontal leg at 60V.