kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
The secondary sees 100% of the load current, but not the full load voltage. So it's only the load current times the voltage difference between in and out.
Still have some confusion here. I went to buckboostcalculator.com which selects units for you based on information you provide and gives you a Square D model(s) transformers and connection diagrams.
With OP's information I come up with needing two 150SV82A units - which would be .15 kVA units connected in an open delta fashion.
Nowhere in product information do I see max overcurrent protection as OP mentions for whatever he has. So what is/how is current rating determined for an auto transformer. I'm guessing kVA rating divided by voltage of any particular coil in the circuit. so the 480 volt portion of a .15 kVA can carry .31 amps, and the 24 volt buck winding can carry 6.25 amps. Now it gets more complicated with three phase with the phase angle involved.