3-phase complex power calculations
roy167
geneva
Hey guys,
I'm looking for resource/book/practice problems/youtube in solving three phase WYE/DELTA, DELTA/ WYE any combination of line/phase voltage current problems for my PE exam. I have no problem with magnitude, I know when to apply root 3 etc, the problem is with angles.
For e.g. Problem like this.
Keep in mind it's been way too long since I've done this kind of math, but since in a delta system Eline = Ephase, wouldn't you just calculate the voltage drop on the feeder resistance/inductance combination and then add that voltage to the Vab given? Someone correct me if I'm wrong.
Ran the numbers and I get 13079.37, which is most close to answer (c)
Hey guys,
Check this post from an old thread. I listed many resources that were helpful for me.
http://forums.mikeholt.com/showthread.php?t=193551&page=2&p=1942434#post1942434
Another resource I did not discover until after the exam:
https://drive.google.com/open?id=1aCbNmsV3mhXHcTASP0WKkcwEubaS7NZU
keep at studying and best of luck in April!! :thumbsup:
I think you are right. The voltage sense it is opposite to the current sense-according the sign convention.
We may transform the sketch from:
If the IaA argument is -20o then the argument of the vector difference IaA-IbB is +10o.:
We may use the sketch from IEEE 141[Figure 3-11Phasor diagram of voltage relations for voltage-drop calculations] modified for φ>0:
Horizont=OB=VAB+AB; AB=AE-CD; AB=I*R*cos(φ)-I*X*sin(φ)
Horizont=VAB+I*R*cos(φ)-I*X*sin(φ)[really]
Vert=GB=GC+CB=I*X*cos(φ)+I*R*sin(φ)[imaginary]
Then Vab=VAB+(I*cos(φ)+jI*sin(φ))*(R+jX)
Going into phasors etc may be little more complicated for problem like this. If delta impedance was given you could convert delta into WYE and solve it for a phase.
how do you solve it for a phase? They have given the delta line current so it would be easy to find phase current and phase voltage drop. The problem is there line impedance in B phase and this is where I don't know what to do.
Can someone help solve it algebraically? Mathematically? Without phasors etc?
Going into phasors is required, it's not an option. Since the line impedance isn't purely resistive, phasors will come into play.
Ladies & Laddies... Here's a shorter way:
Whenever a balanced delta-load is to be analyzed, then. most of the time, the solution is easier if you convert to a balanced 3ph, 4-wire, wye-load circuit ! Now, the circuit can be reduced to single-phase: having one source-voltage, Van; one load-voltage, VAn = VAB/Sqrt(3)! and one line impedance, ZaA !
Facts, derived from the data:
  1. Sequence is un-necessary because circuit is now single-phase!
  2. Load is inductive (lagging) because line-current has a negative angle!
  3. Fact 2 is important because if the current is lagging, then source-voltage is ‘Higher’, than load-voltage!
  4. Thus, you need only calculate the cable V-drop, Dlta-V = IaA x ZaA, in Volts!
  5. Then add Dlta-V, to VAn... not Vab, nor VAB!
  6. Finally, Vab equals Sqrt(3) x (VAn+Dlta-V) !
  7. Hope it helps!
Regards,, Phil Corso
  7. Hope it helps!
If ZAB=ZBC=ZCA=Z and IaA=I>0; IbB=I>-120; IcC=I>-240; then it could be correct. In any different case you need complex "assistance":weeping:.