Line-current, IaA, was equal to 17.2 A<20º !
And yet another mistake. :slaphead:
Seriously, how difficult is it to say "sorry, I made a mistake and came up with the wrong answer"?
Line-current, IaA, was equal to 17.2 A<20º !
D.Lucini
I'm sorry you are displeased! But, I'm at the age where mistakes are a way of life! Hopefully, that's all you will have to face when you're my age!
And, yes, it should have been 72.1 !
The 20 degrees is negative, not positive. As for the solution posted, the E part of your GiFiES was wrong.Sorry fellas...:happysad:
I used my load values in a 3-ph Load-Flow calculator! Line-current, IaA, was equal to 17.2 A<20º ! Referenced load VAB, was equal to 12.5 kV<0º ! Calculated source, Vab, was 13.8 kV<54º ! Furthermore, Other phases were appropriately displaced,i.e, +,- 120deg
Depending on reaction I may show you how it's done using Parameter magnitudes! Even with 2-phases!
And I use a slide-rule ! It as served me well 65 years !:slaphead:
Best of luck !!!
Phil
Gentlemen ?
Here are my final two words on the topic… No, they aren’t Mea Culpa! Instead, they are Astonishment and Surprise!
First, I am astonished that no-one, repeat no-one, noticed that the solution I provided was a D-D analysis, not a D-Y transformation, nor a 1-ph equivalent method, not even the 2-phase approach!
Secondly, I am surprised no-one asked for a copy of my method !
Wait… I erred once again! There is a 3rd comment… I fondly wish that the remainder of your
lives are Healthy, Joyous, and Prosperous !
Phil Corso
Gentlemen ?
Here are my final two words on the topic… No, they aren’t Mea Culpa! Instead, they are Astonishment and Surprise!
Phil Corso
The solution you provided had a formula error. Specifically the "IΔ = IL / Sqrt(3)" is missing a phase shift. Line current into the corner of a delta is not in phase with the delta (phase) current. You know that of course. Otherwise, nothing wrong with your method in general.Gentlemen ?
Here are my final two words on the topic… No, they aren’t Mea Culpa! Instead, they are Astonishment and Surprise!
First, I am astonished that no-one, repeat no-one, noticed that the solution I provided was a D-D analysis, not a D-Y transformation, nor a 1-ph equivalent method, not even the 2-phase approach!
Secondly, I am surprised no-one asked for a copy of my method !
Wait… I erred once again! There is a 3rd comment… I fondly wish that the remainder of your
lives are Healthy, Joyous, and Prosperous !
Phil Corso
The method in general is not the problem. The execution is the problem.What we noticed is that your method produced the wrong load impedance, the wrong load current, and the wrong source voltage.
Your method is, quite frankly, irrelevant since it produces the wrong results.
This whole string reminds me of the proud parents in the stands and as the marching band comes by "Look honey, everyone is out of step except for our son..."
The method in general is not the problem. The execution is the problem.
Line-current, IaA, was equal to 72.1 A<20º ! Calculated source, Vab, was 13.8 kV<54º !
Not sure what is up. So many twists and turns. Where is Robert Stack when you need him?I'm not so sure about that. An execution mistake (missing an angle change) led to an incorrect load impedance of 309<20.
However, even using the incorrect load impedance of 309<20, it would still not lead to these results...
Unfortunately, I'm thinking that the "method" being employed is "trolling."
Junkhouse...
You're getting closer ! Except that your calculated 777 V-Drop isn't added to the Ph-Ph source magnitude (Vab)! Instead it should be added to the Ph-neutral value (Van) ! Then, Van is multiplied by sqrt(3) and the 30 deg angle applied !
Your method negatively impacts the P.L.C. !
Phil
What does that even mean? What does have to do with the circuit analysis and responses?Sorry Luchini,
You and other responders to the OP's question have put me in a precarious legal position !
1)No. To get 120 degree differences you need to take the currents in a symmetric direction. I took them in the direction I used at the time when I summed current.Mivey, Dkarst, et al...
1) Shouldn't all your 'FWIW' Load Phase angles be 120 deg apart? Luchini, what do you think?
2) Exactly what given values led to the idea the load was capacitive?
3) Again I ask, what was is P.L.C. Factor?
4) I did exactly what you suggested! In a computer!
5) What makes you so sure the Identified answer to the Test question is correct?
6) BTW, 7-decimal answers is not proper engineering!
7) If you don't understand my legal dilemma, talk to a lawyer!
More later!