What is an acceptable current unballance on a three phase compressor? I have a fuse that keeps on blowing but when I replace the fuse and put a clamp meter on it it reads fine. One phase though is about 5 amps more than the others.
Acceptable unbalance is 5% for motors.
the devil will be in the details.... 5 amps on a 200 amp compressor is insignificant, on a 10 amp, different story
What is the compressor FLA and what size fuse are you using ?
No, not even close to 5% more like less than 1% before you should start derating the HP of the motor.
That's for source VOLTAGE unbalance. The 5% was a value recommended by Franklin Electric on measured CURRENT unbalance.