3 phase current draw from 3 xformers
dm9289
Industrial Maintenance Electrician
Pennsylvania
Industrial process repair/ maintenance Electrician
Where I work we are rerouting and dividing some cabling and I came across a 3 phase calculation that stumped me let me build it below
Low voltage switch gear 480V Delta ungrounded
Phase A B C
3 Transformers fed by
AB BC AC
Output to 3 fixed loads 600a 600a 600a
240volt 2 wire each
My question is given I know when the heating grids are fed with 240v I will get 600a current draw how much current will each phase see on the 480 delta ?
I wanted to simply amp clamp this but this could not be done due to company safety regulations plus I could not remember how to calculate this.
Thanks
Dave
Correct 600a 240 volt single phase on the secondary side what I am trying to calculate is primary current on 480 3 phase side. There are 3 heating grids each draw 600a at 240v
So I should suspect the clamp on amp meter to read 1038 amps on each phase 480v side and size conductors accordingly
If I understand the question correctly: 520 amps on the primary side.
Primary of each transformer 300A 480V 1? and where lines are separate from other transformers. On the line (supply) side of where/if joined, it will be 520A.
Each individual primary circuit will draw 200 amps. If all three of those circuits are balanced across a three phase system the system will see 520 amps per phase at what ever point each load becomes common (or starts to share conductors) to one another and from there back to the source. Phase A is seeing some current from B and some from C as well as the contribution to the load coming from A. If everything is balanced that 1.732 is the factor you use to determine what value is measured on A, and you don't even need to fully understand the phase angles and how they play a part in this. Start unbalancing things or throwing in non linear loads and it gets more complex. Same applies to the other two phases.
would it depend on if all three grids are on at the same time, not sure how the grids are controlled. wouldn't the answer be worst case 600 and the answer somewhere between 520 and 600 amps
sorry I didn't see post# 12 when I posted. already answered
600 amps @ 240 volts is 144kw.
144kw/480=300 amps single phase on the primary side of the transformer.
let say we have a three phase delta to delta transformer and the load is wired in delta:
3x144kw is 432kw/240/1.732= 1039.2 amps secondary load.
And 432kw/480/1.732= 519.6 amps primary load.