SAWMILL TECH
New member
- Location
- Owego New York
We have just recently purchased a new plant where I have run across a situation where I'm not comfortable or knowledgeable with. The plant has a 480 volt 1200 amp service feeding it. One of the branches feeds a 75KVA, three phase, delta to delta, 480 volt to 240 volt with a center tap on the secondary for 120 volts. There is no equipment in the plant that uses three phase 240, everything has been converted to 480 volt over the years. The only thing the transformer feeds is some 240/120 single phase panels using the center tap as neutral. The transformer's primary is protected, the center tap is grounded. I'm not sure of how to rate and protect the secondary with the center tap (5% of total KVA comes to mind but I'm not sure). Transformer is old and it's been impossible to get in contact with Square D support. Also I am having trouble finding any reference to this situation in the NEC. I believe the secondary is not protected right or I can even use this transformer in this application.