Hey Everyone im new to the forum but have been looking up questions on here for years! Hopefully i can gain some wisdom from everyone! Thanks in advance!
I need to wire 3 tesla chargers in an older warehouse that has a 3 phase Delta system. Another electrician ran a 200 amp single phase panel with the A phase, B phase(high leg), and ground (no neutral in the panel). If I understand correctly on the other forum questions I've seen, I should be ok to run the 3 2pole breakers needed, on this panel right?
I need to wire 3 tesla chargers in an older warehouse that has a 3 phase Delta system. Another electrician ran a 200 amp single phase panel with the A phase, B phase(high leg), and ground (no neutral in the panel). If I understand correctly on the other forum questions I've seen, I should be ok to run the 3 2pole breakers needed, on this panel right?