Hey Everyone im new to the forum but have been looking up questions on here for years! Hopefully i can gain some wisdom from everyone! Thanks in advance!

I need to wire 3 tesla chargers in an older warehouse that has a 3 phase Delta system. Another electrician ran a 200 amp single phase panel with the A phase, B phase(high leg), and ground (no neutral in the panel). If I understand correctly on the other forum questions I've seen, I should be ok to run the 3 2pole breakers needed, on this panel right?
 
No sure about the chargers. As far as I know they are just standard tesla chargers.

Yes I do agree about the 3 phase panel. I am coming into this project as the 2nd electrician so I'm trying to figure out some stuff that the original guy did.
 
If I understand correctly on the other forum questions I've seen, I should be ok to run the 3 2pole breakers needed, on this panel right?
Yes this is fine. Note you will need straight, not slash rated breakers. It is usually cheaper to just use 3 pole breakers. If it happens to be a Siemens true panel board, you can use a BQD 2 pole breaker
 