In sizing conductors for a 3-phase delta service that will have no neutral load I was assuming my neutral conductor size would only have to be not less than the GEC, 250.24(C)?
But then I saw 250.24(C)(3) Delta-Connected Service.
Says the neutral shall have an ampacity not less than the ungrounded conductors.
Am I reading this correctly? If so why does the neutral have to be sized that way?
My loads are all 3-phase 240 volt, they don't need a neutral.
Thanks
But then I saw 250.24(C)(3) Delta-Connected Service.
Says the neutral shall have an ampacity not less than the ungrounded conductors.
Am I reading this correctly? If so why does the neutral have to be sized that way?
My loads are all 3-phase 240 volt, they don't need a neutral.