Really, I am not trying to be pedantic. Preventing misunderstandings is one reason there are IEEE/ANSI standard methods for describing voltage systems.
jim dungar said:Really, I am not trying to be pedantic. Preventing misunderstandings is one reason there are IEEE/ANSI standard methods for describing voltage systems.
The 240/120 3PH 4W delta system produces a nominal 208V to ground/neutral conductor from the high leg. To call it anything else adds confusion and misinformation as well as violates the NEC
208Y/120 is not more 'correct;' they're different systems. The 4-wire high-leg services I've seen almost always have a larger 120/240v 'main' transformer and a smaller high-leg unit for the 3-ph loads.There's no 'imbalance' for a system designed for the loads.acrwc10 said:I am feel the imbalance caused by using only 2 of the 3 phases is a big issue with this installation if they do not correct the system to a 120/208 Y.
Really? There have been several higher-voltage-first-for-3ph/lower-voltage-first-for-1ph discussions here about how to describe the supply. I'm suprised you haven't noticed (or remembered.)iwire said:I never knew there where standard ways of posting voltages until you brought it up.
220/221 said:I don't know what nominal means and I have no desire to look it up.
Additional translation: Don't confuse the issue with facts.roger said:Translation: It is my God given right to shut the door on education and remain ignorant, I dare someone try to point me in the right direction.
LarryFine said:208Y/120 is not more 'correct;' they're different systems. The 4-wire high-leg services I've seen almost always have a larger 120/240v 'main' transformer and a smaller high-leg unit for the 3-ph loads.There's no 'imbalance' for a system designed for the loads.
Translation: It is my God given right to shut the door on education and remain ignorant,
220/221 said:I don't know what nominal means = I don't know what nominal means.
I have no desire to look it up = I have no desire to look it up.
codeunderstanding said:What if you had a 120/208v system and needed to add a subpanel out of a main panel. The only things needed to be ran off the subpanel were single pole loads like lights, receptacles, and baseboard heat would it be better to just a single phase panel, or would you have to add the three pase panel to balance between the three phases?
acrwc10 said:Just my opinion, it would be irresponsible to put in a single phase load center if you had a 3 phase service, unless it was a residential setting.
It depends on how the system was loaded and how much load you intend to put on the 120/208 volt single phase panelboard. We permit 100 ampere commercial services on 208Y/120 volt transformers but our smallest transformer is 75 kVA (normally larger) and the demand would only be 40 amperes maximum (our demand factors, not from Article 220). If you put a small load on the two lightest loaded phases, I don't see a problem. :smile:codeunderstanding said:. . . wouldn't that make the system unbalanced if you did. . .
Which pretty much proves Roger's point.
would it be better to just a single phase panel, or would you have to add the three pase panel to balance between the three phases?