There is an exception to the three phase MWBC and I beleive it is in the 2008 code somewhere.
In technical installations, computer centers, broadcast plants, call centers, anywhere there is a large collection of electronic equipment. You always pull a neutral per circuit and in addition I always spec 1.5 to 2x awg for the panel neutral feeder.
The problem is harmonic current caused by rectification in power supplies which does not cancel out. There have been several documented cases in the 70s of red hot neutral bars, literally glowing red, in computer centers and other high density electronics installations.
And where you have sensitive analog electronics, shared neutrals are an excellent to way to transmit ground noise.