3 phase equipment

Status
Not open for further replies.

wireperson

Senior Member
Location
Florida
1. what happens if I feed a 3 phase condensing unit using a 3 pole breaker in a single phase panel? its just causes phase imbalance on panel? or damage the CU?.


2. what happens if the same condensing units is fed by a 2 pole breaker , you left 1 of the phases without wire.

I was working in a CU today and found that they have 2 CU's (both 3 phase). 1 of them (cu1)is being fed from a 3 phase panel using a 3 pole breaker. . .that's ok .The other one (cu2)is fed from a single phase panel and the missing phase is shared from cu1 , besides they are unsing single pole breakers on this 1 phase panel . That's the reason of the 2nd question , because when they turn off the breaker on cu1 the cu2 will be missing 1 phase. . . . . . any thoughts?
 
Since its a motor for the condensor, yes it not correct to be only on a breaker usually its a fused application with anything from 125 to 200%, Dual element time delayed, etc... I'm not sitting with a Code book ...
Someone please state a Code Article ...

In most cases your in-rush of current caused buy a motor will overwelm a three pole breaker.

Now you can breaker the branch circuit thats infront of the disconnect, but this doesn't seem to be the case.
 
If control voltage (phase monitor or improper primary voltage on a control transformer) did not stop the unit from starting, I would think you would have single phasing of the compressor which would result in damage to the compressor.
 