M mobo Member Location MO USA May 10, 2022 #1 Hi, wondering......if a generator's voltage selector switch is set on 480/277, can you hookup a 480V 3-wire load to it safely? Just, of course, leave off the neutral?
Hi, wondering......if a generator's voltage selector switch is set on 480/277, can you hookup a 480V 3-wire load to it safely? Just, of course, leave off the neutral?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician May 10, 2022 #2 Portable generator? If it is the neutral would typically be bonded in the generator and you would be good to go.
Portable generator? If it is the neutral would typically be bonded in the generator and you would be good to go.
M mobo Member Location MO USA May 10, 2022 #3 ActionDave said: Portable generator? If it is the neutral would typically be bonded in the generator and you would be good to go. Click to expand... Yes, it's a portable.
ActionDave said: Portable generator? If it is the neutral would typically be bonded in the generator and you would be good to go. Click to expand... Yes, it's a portable.