Just don't underestimate the phase imbalance issues. This might not apply to you situation, but saw a facility with utility power and genny backup. 3-ph 480V going to a number of air compressors with Wye-Delta starters, and 1-ph 480 going to the primary of a 480/120-240 transformer going to an MCC. Everything was fine until one day the utility power was shut off for an upgrade. The Wye-Delta starters had a delay that was long enough that only the single phase transformer loaded the genny. The genny saw an imbalance long enough to shutdown, which was before the 3-ph air compressors came on. The work around was to open the primary breaker to the 1-ph transformer until an air compressor kicked in, then energize the transformer thereby feeding the MCC. The imbalance setting was changed to a higher setting (I forget just what, now) as a fix, at least temporarily.
With three buildings in your design, might never be an issue, but if for some reason two buildings are shutdown, it could be.