Yes, my mistake. 30A is the line current. The coil current would be 30A / sqrt(3) = 17.3A.You have a 240 delta machine that is 10 kW / 12.5 kVA.
That is 30 amps per corner on 3 phase loads. Because each corner is being supported by both sets of windings. The individual windings carry less than the full 30 amps.
OK, but 20A is greater that the 17.3A maximum coil current from a balanced 12.5 kVA 3 phase load. So wouldn't the maximum single phase current be 17.3A * 1.5 = 26A?If you take single phase load from 2 corners, the max is still 30 amps due to total heat dissipation in the windings.
The in-phase winding will be carrying 20 amps, and the out-of-phase windings will be carrying 10 amps.