slipknotbmg
Member
We have a 3-ph. 1800A 480V service coming into an MCC w/ a adj. trip GFCI main Brkr. Inline C.T.'s on 3-ungrounded and 1 grounded conductor. Our descrepancy is where the main bonding jumper should be located. I think on the service side of the ungrounded conductor before the Neutral C.T. assuming in a ground fault condition the breaker will operate normally and trip regardless of condition or even the existence of the CT. Another Forman is arguing that in order for the GFCI main to detect a ground fault, the bonding jumper needs to be on the secondary side of the CT. Any opinions would be greatly appreciated.