Other way around isn't it?
If problem follows the wire the problem is with the source.
If it stays the same problem is with the motor.
That sounds assuring.
Other way around isn't it?
If problem follows the wire the problem is with the source.
If it stays the same problem is with the motor.
Other way around isn't it?
If problem follows the wire the problem is with the source.
If it stays the same problem is with the motor.
The 5% limit only applies to a single three phase transformer that supplies the wild leg system. I have never seen such a transformer, but know they exist.
The utility will use two or three transformers for this type of service with a larger one supplying the 120/240 volt single phase loads. Around here that type of service is typically used where the 3 phase load is very small as compared to the single phase load. Most often they will install this as an open delta. The local utility calls the two transformers the "lighter" and the "kicker", with the lighter supplying the single phase loads and the kicker adding the third phase for the 3 phase loads. Of course that doesn't mean that the single phase loads have not been expanded to the point where they caused the voltage imbalance, but I would expect two legs with a lower voltage if that was the case.
Seattle city light calls them "lighter" and "teaser"
http://www.seattle.gov/light/engstd/docs2/0125.02.pdf
Also SCL usually connects these to two phases and the neutral which I think is technically called open wye not open delta?
180819-1930 EDT
This morning I mace some voltage measurements at our shop where we have a 240 V open delta. Total kVA possibly 250 or somewhat higher with about 2/3 for the single phase transformer, and 1/3 for the stringer transformer. I can't read the transformer labeling.
I have no way to make simultaneous measurements, but my results were Vab = 241.3, Vac = 241.4, and Vcb = 241.2 . The maximum calculate phase deviation from 120 degrees was 0.041 degrees.
There is one building tenant with at least a third of the building that was open with all lights on, and air conditioning. I have no control of this load.
cpinetree we need a redo of the voltage measurements with no load on the power company transformers.
.
Taken from Franklins AIM for their pump motors.
"...4. Current unbalance should not exceed 5% at service
factor load or 10% at rated input load. If the unbalance
cannot be corrected by rolling leads, the source of
the unbalance must be located and corrected. If,
on the three possible hookups, the leg farthest from
the average stays on the same power lead, most
of the unbalance is coming from the power source.
However, if the reading farthest from average moves
with the same motor lead, the primary source of
unbalance is on the “motor side” of the starter. In this
instance, consider a damaged cable, leaking splice,
poor connection, or faulty motor winding."
Here is the message that has just been posted:***************
---Quote (Originally by gar)---
180816-1729 EDT
Something is very wrong.
The sum of the voltages around a delta has to equal zero. ...
---End Quote---
Still true if it's an open delta?
***************