3 phase line in swapping with a VFD

Learn the NEC with Mike Holt now!
Status
Not open for further replies.
I was relocating some press rollers recently. Cabinet was 3 phase and contained a VFD.

Basic controlls:

Button 1 raise the rollers
Button 2 lowers the rollers
Joystick up forward motion
Joystick down reverses motion.

When we applied power (BOY), the buttons were reversed, yet the joystick were working as labeled.

We swapped two legs and that fixed the issue. Buttons acted as they should have. And the joystick still operated as before, correctly.

I imagine swapping legs does not effect the VFD and assume that the buttons were independent of the VFD and on a transformer.

Any insight would be appreciated

Sent from my SM-J337V using Tapatalk
 
Just a guess, but the rollers up/down was with a regular contactor type control (across the line...no VFD) so phase sequence matters. The joystick control for forward/backward is controlling the VFD which does not care about phase sequencing at the input to the VFD. So swapping phases matters to the up/down, but not for the forward/reverse.
 
With rare exceptions (cycloconverters) which you are very unlikely to see a VFD converts to DC then back to AC so the input phasing doesn’t matter at all.
 
Yeah, the VFD always puts out clockwise rotation regardless of input. This makes finding correct rotation when hooking up temporary generators much more difficult. We used to check the indoor fan rotation on RTU’s to verify correct rotation, but many manufactures and retrofit applications are using VFD’s to control the fan. The compressor itself is still straight contactor control, so it could be running backwards even though the fan is running correctly.
 
Input power rotation to the VFD is totally irrelevant, all the VFD does is convert it to DC.

Output power can be chnaged on programming, no need to swap conductors. There will be a parameter that you can use to tell the VFD what rotation to give to the motor.
 
Input power rotation to the VFD is totally irrelevant, all the VFD does is convert it to DC.

Output power can be chnaged on programming, no need to swap conductors. There will be a parameter that you can use to tell the VFD what rotation to give to the motor.
Now that you said that, I do remember years back when we were installing vfd’s on exhaust fans for a refrigeration rack room, I was able to change the rotation in the setup menu, and didn’t have to swap wires. We don’t do a whole lot of vfd work. Big Ass Fans is the last vfd’s I had to work with.
 
Now that you said that, I do remember years back when we were installing vfd’s on exhaust fans for a refrigeration rack room, I was able to change the rotation in the setup menu, and didn’t have to swap wires. We don’t do a whole lot of vfd work. Big Ass Fans is the last vfd’s I had to work with.
Or with many you can just move your single direction input lead to the reverse terminal instead of the forward terminal.
 
Or with many you can just move your single direction input lead to the reverse terminal instead of the forward terminal.
If running directly from keypad you might be set up that you can use a forward or reverse labeled button on the keypad.
 
If running directly from keypad you might be set up that you can use a forward or reverse labeled button on the keypad.

Most of them are selectable just by changing a parameter.
Local - Key Pad
Remote - Field Wiring (IE: Discrete Digital Input)
Comm - Err -Communications Network
 
Most of them are selectable just by changing a parameter.
Local - Key Pad
Remote - Field Wiring (IE: Discrete Digital Input)
Comm - Err -Communications Network
Correct. some don't even have definite function for some or even all the inputs and function can be selected via parameters.
 
Correct. some don't even have definite function for some or even all the inputs and function can be selected via parameters.

I've worked with Siemens Master Drives and Vector Control Drives that actually take that concept one step further by enabling the user to select exactly how they want to use the I/O. Any terminal can be Input, Output, Voltage or Current. - Those are a PITA to program.
 
I've worked with Siemens Master Drives and Vector Control Drives that actually take that concept one step further by enabling the user to select exactly how they want to use the I/O. Any terminal can be Input, Output, Voltage or Current. - Those are a PITA to program.
I never used a Siemens drive.

Also seem to find most Siemens products to be a PITA.
 
one step further by enabling the user to select exactly how they want to use the I/O. Any terminal can be Input, Output, Voltage or Current. - Those are a PITA to program.

I though about getting one of these personally just to tinker with since I like Arduino. Anybody ever use these? My first impression was that they were mickey-mouse toyish but, after reading I don't think that's the case. Just non proprietary, which could be good or bad.

https://www.automationdirect.com/videos/video?videoToPlay=kPIZK1tTxvo
 