Did I do this correctly ? Air Compressor with a 3 phase induction motor, 10 hp, 230 v, S.F.A 30.8, Duty Cont., EFF 90.2 %. I ran #6 on a 60 amp breaker, then to a fusible 60 amp disconnect. I asked an electrical contr. friend who does a lot of commercial work, he said the machine will have a thermal protector on it. He said what I have is good. I asked if I needed to downsize the fuses. Your advice ? Thank you.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
You could but not needed.
See NEC Table 430.250 Nameplate SFA is not included in your Calculations
You should already know if the compressor has a starter with overloads just, by doing the work. The mfg would have installed the correct overloads and thermal if one was used.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
A little more investigation is warranted but I lean toward Tom's answer (#3). Most 3 phase 10HP compressor I have seen have a factory starter with overloads but you do need to verify.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
And 175% for time delay fuses gives you 49 amps, so a 50 amp fuse is supposed to be the max, unless it won't hold during starting then you are allowed to increase.
Since he has a 60 amp circuit breaker (up to 250%) the fuse size seems to be irrelevant.
 

kwired

Electron manager
Location
NE Nebraska
Since he has a 60 amp circuit breaker (up to 250%) the fuse size seems to be irrelevant.
Guess so. Kind of makes it pointless to use a fused disconnect unless some sort of supplemental protection is going on or if there were say a feeder tap situation.
 