Taylorwoorobertson
- Kansas
I have a 15 HP 3 phase motor 120/208 v...What are the full load amps?
Based on T. 430.250 it is 46.2 ampsI have a 15 HP 3 phase motor 120/208 v...What are the full load amps?
That's 200Vodd - my chart says 48.3.
Yes it does. The nec tells us to use the tables in the book. 3 phase 208V 15 hp is 46.2 ampsDoes the fact that it is 120/208 make a difference vs 120/240?
By the way, forget the 120V issue, the motor couldn't care less about the phase to neutral voltage, you are just going to confuse yourself. If you have a 208Y120 3 phase 4 wire system, your 3 phase motor voltage is 208V.Does the fact that it is 120/208 make a difference vs 120/240?
I did not take the OP to mean the motor was 120/208 but that that was the system voltageIs this a test question? Where did you ever get a 120/208 motor?
As stated:I did not take the OP to mean the motor was 120/208 but that that was the system voltage