I am currently bidding a job which requires running branch circuits to 2 5ton ac condensor units.The utility served the building with 120/240 delta.The only 3 phase load existing is a 60 amp elevator.The buildind is a huge church.They have a 240 volt pipe organ,8 heating air handlers 12 amps each at 120 volts,church lighting and numerous recepts in the kitchen and dining hall which may have as many as 10 electric grills plugged in during certain baking events.During the air conditioning season we will only be using 2 air handlers.Because of the high leg we only use the A and C phases except for the elevator.The church service is 200 amps.The single phase min. circ. ampacity on the condensors is 34 amps each, and the 3 phase mca for each is 21 amps.The 3 phase units will cost 1000 dollars more for both units.I want to use 3 phase units because I'm afraid of possible service overload in future if I use single phase.I'm going up this morning to do a service load amp reading while church services are in progress.Besides wire size will you guys help me explain the advantages of going 3 phase?Possibly savings in the electric bill or life of 3 phase motors over single phase.I want to justify using the 3 phase motors in an econical sense.Thanks for your help.