So does running it over base speed by frequency change.increasing speed mechanically would reduce torque proportionally
We did quite a few in the 56kW to 200kW typically capable of 20,000 to 30,000 rpm for machine tool applications but I agree with you - these are special purpose and relatively rare applications in the great scheme of things.
I also wonder why a gearbox/v-belt/morse pulley arrangement wasn't used. Space maybe? Perhaps the OP knows the reasoning behind that.
Not unless you double the voltage.The faster the motor goes, the greater the horsepower/kw you can get out of a give frame size.
Double the motor speed and you double the horsepower.
Not unless you double the voltage.
IIRC OP said this runs around 3000 RPM. I can only recall seeing 4 pole motors in the HP range OP is dealing with, and have a suspicion that a 2 pole is either non existent or not so easy to get, and could be a factor in why they are overdriving the one they have instead of using a 2 pole and slowing it down to what they need.I see that people have a hard time with this concept, but honestly, it's done all the time with no significant issues.
In this application with shear rollers that need to run at different speeds, the mechanical designer had two choices; run the top roller at full speed and use gear reduction to slow down the bottom one, or run the bottom one at full speed and increase the speed of the top. Slowing down the bottom means lower throughput (by comparison). So then increasing the top speed has two choices; use a gearbox to increase the speed, or use a VFD. The gearbox results in less torque, so they must start with a larger motor, then get lower operating efficiencies. Increasing with a VFD would result in lower torque /larger motor, ULESS you do the voltage trick. So all in all it's the best choice.
There has already been some very good info posted.-Jon
I see that people have a hard time with this concept, but honestly, it's done all the time with no significant issues.
In this application with shear rollers that need to run at different speeds, the mechanical designer had two choices; run the top roller at full speed and use gear reduction to slow down the bottom one, or run the bottom one at full speed and increase the speed of the top. Slowing down the bottom means lower throughput (by comparison). So then increasing the top speed has two choices; use a gearbox to increase the speed, or use a VFD. The gearbox results in less torque, so they must start with a larger motor, then get lower operating efficiencies. Increasing with a VFD would result in lower torque /larger motor, ULESS you do the voltage trick. So all in all it's the best choice.
Everyone explained how this works so I won't add to that. But no one mentioned how your mfgrer cheated you out of not only your "free" Xtra hp, but also baseline rated torque.At the plant I work at we have a piece of equipment that came from the manufacture with a 50HP 3 phase motor wired for low voltage (I need to verify this, not sure on the voltage) that is controlled by a VFD that is supplied with 480vac. The motor nameplate parameters in the VFD list the motor as being 45kW, 84 FLA, 460V, 104Hz, 3016 rpm. I am waiting for the machine to shut down so I can grab the actual nameplate data off of the motor.
I really didn't understand a whole lot about this and how it is done. I ran across the following post by Jraef in an older thread that helped me to understand things a little better. http://forums.mikeholt.com/showthread.php?t=115549&page=2&p=1074268#post1074268 Post 18 if it doesn't take you to his post. The manufacture is based out of Germany (equipment for chocolate refining) and the tech that flew over here tried explaining this to me a few months ago but he/what is was explaining was difficult to understand.
What Jraef described matches the setup I believe I am dealing with. The manufacture uses a motor that is undersized for the application, not 100% sure why they do it this way, I know a larger motor and gearbox probably wouldn't fit in the machine so that might be a reason. I believe they also do this to gain a higher speed. We constantly run this motor between 85 and 104Hz
Anyways my question is, what affect does this have on the current that the motor pulls? How would you size the VFD for this application? The VFD that is used is I believe rated for 150-200HP.
We have 1000+ motors and a couple hundred VFDs at my plant but this is the only one setup like this.
Thank you for your time!