JFletcher
Senior Member
- Location
- Williamsburg, VA
Although you could get away with as few as 4 ungrounded conductors, and 2 grounded conductors with the EMT as the ground, in this application I would run 4 Hots 4 neutrals and one ground wire. the reasons being that wow multiwire Branch circuits are certainly elegant, the fourth circuit kind of bugs that up. Yes, you will use more wire in this case however you can put those for circuits in the panel anywhere they may fit, and there may not be room in the existing panel to put a triple pole breaker in. if you use a neutral for each circuit, you don't have to worry about some idiot down the road breaking the neutral and sending higher than intended voltage to one or more phases. Also, while and EGC is not needed here, I'm of the camp that redundancy is good, and I have seen too much EMT improperly assembled or damaged, or corroded that it as a ground path would be compromised
although not applicable to your installation, many job specs now forbid multiwire Branch circuits, and for the reasons I mentioned.
on the extremely off-chance that you are installing medical equipment in a hospital, not only will you need and EGC you will need a second ground pathway as well.
, PS Welcome to The Forum aren't you glad you asked the question now LOL
edited to add... no matter if you use 6 current carrying conductors orate here 6 wires or 9 you're still within fill limits and can still use 20 amp Breakers either way.. it's a matter of personal preference and your existing set up really
although not applicable to your installation, many job specs now forbid multiwire Branch circuits, and for the reasons I mentioned.
on the extremely off-chance that you are installing medical equipment in a hospital, not only will you need and EGC you will need a second ground pathway as well.
, PS Welcome to The Forum aren't you glad you asked the question now LOL
edited to add... no matter if you use 6 current carrying conductors orate here 6 wires or 9 you're still within fill limits and can still use 20 amp Breakers either way.. it's a matter of personal preference and your existing set up really