I need some help (and no not that kind). I just finished wiring up a YORK rooftop HVAC unit with electric heat strips and a VFD controlled blower motor. The building is fed with a 3 Phase 4 wire 120/240 Volt open delta service which has a high B phase.
The drive has an annoying habit of tripping out on "phase loss or imbalance". I added a drive isolation transformer (which I had to do on a TRANE unit installed on the same building, and on the Trane the transformer fixed the problems). This unit still trips out regularly. I have measured the voltages on both sides of the transformer, and the phases are not exactly balance from phase to phase as in say 242, 250 and 256 on the primary side, this of course affects the balance on the secondary side.......
Tech info :
Drive: DELTA MS-300 series
Motor: BALDOR 3Hp air over motor SF=1.15
Service notes: 4 single phase items on the transformer bank..... a) masonic Lodge no A/C units visible from the exterior, b) street light and special event receptacle panel c) 2 special event services with receptacle panels on the building. The special event stuff had no loads on them at this time.
Any ideas how to get this working? I hate to do buck boost transformers on each leg, ans there is no guarantee that come summer I wont have to change things. The power company is saying for about 20k, they can give us a wye service...... Seeing as this is a municipal building that isnt really in the budget
de, Howard
PS: why do I get all the "dirty dogs" at the shop lately????????
The drive has an annoying habit of tripping out on "phase loss or imbalance". I added a drive isolation transformer (which I had to do on a TRANE unit installed on the same building, and on the Trane the transformer fixed the problems). This unit still trips out regularly. I have measured the voltages on both sides of the transformer, and the phases are not exactly balance from phase to phase as in say 242, 250 and 256 on the primary side, this of course affects the balance on the secondary side.......
Tech info :
Drive: DELTA MS-300 series
Motor: BALDOR 3Hp air over motor SF=1.15
Service notes: 4 single phase items on the transformer bank..... a) masonic Lodge no A/C units visible from the exterior, b) street light and special event receptacle panel c) 2 special event services with receptacle panels on the building. The special event stuff had no loads on them at this time.
Any ideas how to get this working? I hate to do buck boost transformers on each leg, ans there is no guarantee that come summer I wont have to change things. The power company is saying for about 20k, they can give us a wye service...... Seeing as this is a municipal building that isnt really in the budget
de, Howard