H1 & H2 are labeled incorrectly and don't follow IEEE guidelines.
The primary is drawn like open delta, the secondary is all screwed up.
Three bushings yet two designations. X0 is a common point and is generally found on pad mounts where the coil windings are internal and can't be changed as easily as a single transformer.
Also, the secondary bushing on the right transformer is missing a lead. It needs to be tied to the other transformer secondary lead.
So for that one I see a single phase 240 volts, but there will be no high leg voltage because the coil is floating and doing nothing.