Biogas Sparky
- Redding
- Industrial Electrician
Hi everyone.
I have been working on this calculation for a few days and am curious if it have it correct, so any help would be greatly appreciated.
We have a system that we are designing/ building for biogas clean up. This system is mostly motors that come as pre-assembled systems. For example, one system has a 200hp, 10hp, 7.5hp, and 1/2hp 3phase 480 volt motors, the manufacture supplies the control enclosure for all these with the 200hp VFD controlled. All the motors for the whole system are continuous and run simultaneously.
Here is the calc chart that I put together for this. I hope this makes sense. I multiplied the largest motor by 1.25 in the VA column and then the total VA by 1.25 as it is all continuous load that I know of currently (I will adjust if anything is not continuous)
Thanks in advance for the help.
| Main Equipment | Equipment Loads | HP | FLA | Volts | Multiplier | va |
| Intake Blower Skid | ||||||
| Blower | 20 | 27 | 480 | 1.732 | 22446.72 | |
| AA | 2 | 3.4 | 480 | 1.732 | 2826.624 | |
| Feed Gas Compressor 1 | 480 | 0 | ||||
| Screw Compressor | 200 | 240 | 480 | 1.732*1.25 for largest motor | 249408 | |
| Gas Cooler | 10 | 14 | 480 | 1.732 | 11639.04 | |
| Oil Cooler | 7.5 | 11 | 480 | 1.732 | 9144.96 | |
| Condensate Pump | 1/2 | 1.1 | 480 | 1.732 | 914.496 | |
| Product Gas Compressor | 480 | 0 | ||||
| Compressor | 50 | 65 | 480 | 1.732 | 54038.4 | |
| Cooler | 5 | 7.6 | 480 | 1.732 | 6318.336 | |
| Pre lube | 1.8 | 480 | 1.732 | 1496.448 | ||
| Oil Heater | 1.8 | 480 | 1.732 | 1496.448 | ||
| Chiller | 480 | 0 | ||||
| Potential | 50 | 480 | 1.732 | 41568 | ||
| Transformer 1 | 25 kva | 52 | 480 | 1 | 24960 | |
| DCP1 | 120 | 0 | ||||
| Heat Trace | 120 | 0 | ||||
| UPS/ Network | 120 | 0 | ||||
| Exterior Lights | 120 | 0 | ||||
| Gen Recp (1) | 120 | 0 | ||||
| 0 | ||||||
| 0 | ||||||
| 0 | ||||||
| O2 Container | 0 | |||||
| Compressor | 25 | 34 | 480 | 1.732 | 28266.24 | |
| Transformer 10kva | 20 | 480 | 1 | 9600 | ||
| Totals FLA | 585.1 | 464123.712 | ||||
| Total VA/ 831 | 558.5122888 | |||||
| Total FLA *1.25 for continuous load | 731 amps | Total VA/831*1.25 for continuous load | 698 amps |