Worked at a business that is going to have a mini-split installed.
My task was to run a new circuit to the outside with disco.
![100ampbreaker.jpg 100ampbreaker.jpg](https://forums.mikeholt.com/data/attachments/16/16343-1b5b38e33a28ea9ea32811b278298d7c.jpg)
![3-phase panel.jpg 3-phase panel.jpg](https://forums.mikeholt.com/data/attachments/16/16344-9d24912a6680c7c9900f8780136b2d23.jpg)
When I pulled the panel cover off the first thing that caught my eye was the 100 amp breaker with a jumper. At first I didn't know what to think. Then when I looked at the conductors feeding the panel I realized it was a 3-phase panel.
I already knew this building was supplied with only single phase. It's an older strip mall type of structure and I've done work in some of the other units. All the other units I've been in had single phase panels.
It's strange that this unit had this panel.
Regardless, there was no markings (or warnings!) about this setup and the fact that phase B and C are the same phase....
The way I see it, all the breakers that are in the "C" location are being fed by the jumper wire on the 100-amp breaker. And if you put a 2-pole breaker in a spot that is a B phase and C phase you're feeding that load with the same phase....
Obviously a variety of violations,
How serious would you consider each item?
My brain keeps going back to the jumper wire on the 100 amp breaker. I'm not sure what size it is. Maybe #4 at most.
My task was to run a new circuit to the outside with disco.
![100ampbreaker.jpg 100ampbreaker.jpg](https://forums.mikeholt.com/data/attachments/16/16343-1b5b38e33a28ea9ea32811b278298d7c.jpg)
![3-phase panel.jpg 3-phase panel.jpg](https://forums.mikeholt.com/data/attachments/16/16344-9d24912a6680c7c9900f8780136b2d23.jpg)
When I pulled the panel cover off the first thing that caught my eye was the 100 amp breaker with a jumper. At first I didn't know what to think. Then when I looked at the conductors feeding the panel I realized it was a 3-phase panel.
I already knew this building was supplied with only single phase. It's an older strip mall type of structure and I've done work in some of the other units. All the other units I've been in had single phase panels.
It's strange that this unit had this panel.
Regardless, there was no markings (or warnings!) about this setup and the fact that phase B and C are the same phase....
The way I see it, all the breakers that are in the "C" location are being fed by the jumper wire on the 100-amp breaker. And if you put a 2-pole breaker in a spot that is a B phase and C phase you're feeding that load with the same phase....
Obviously a variety of violations,
How serious would you consider each item?
My brain keeps going back to the jumper wire on the 100 amp breaker. I'm not sure what size it is. Maybe #4 at most.