Is permitted by NEC to serve a dwelling unit with 3-phase power say 208Y/120V
What about feeding the apartment with 208Y/120 3PH 4W makes sense... over 120/208 1PH 3W?... I have a project (227 units, one building) where it makes scene to feed the apartment with 3-phase feeder...
In many instances there likely isn't enough load in each individual unit to justify cost of three phase gear for individual units and there almost is never any three phase loads to feed within the dwelling units themselves. But you do have larger conductors to run for feeders if only supplying same VA with single phase - but in many cases still will be 100 or 125 amp panelboards just with one less bus. Put in a 60 or 80 amp main you still likely have 100 or 125 amp bus as that is typically all they make for them.thanks everyone for your valuable inputs. our project will be served by (4) 2500A, 208Y/120V services at 4 different locations. I think I will propose the 3-phase option, especially that i will be running a larger (300 Amps) riser to feed 5 stacked units (5-story Building) and tap-off at each level with smaller feed to each apartment panel (80A 3-phase or 125A 1-phase)
Is permitted by NEC to serve a dwelling unit with 3-phase power say 208Y/120V
thanks everyone for your valuable inputs. our project will be served by (4) 2500A, 208Y/120V services at 4 different locations. I think I will propose the 3-phase option, especially that i will be running a larger (300 Amps) riser to feed 5 stacked units (5-story Building) and tap-off at each level with smaller feed to each apartment panel (80A 3-phase or 125A 1-phase)
How are you metering if using common feeders?
Here the law requires individual metering for each dwelling unit.
Perhaps they are unmetered, as are all the apartments here. Our monthly fee includes water, sewer, and electric. Everything but phone and Internet. It surprised me too.
My first though would be the availability of a service drop. A dwelling unit usually is located in a residential neighborhood and if 3ph would even be available where an apartment complex may be more in an industrial commercial area where 3ph is available.
It is of my opinion that Bering allowed is not the issue but sourcing the 3ph to begin with.
Why wouldn't there be three phase primary in a residential neighborhood? May not be present adjacent to each lot but chances are it isn't too far away.
Same here, but if a customer is willing to add the load to the system they will build it - may be some cost to the user though. This is nothing inside a city or small town compared to when some rural customers need such improvements to get what they need for power. If they run three phase primary down the road they will alternate phases when connecting single phase loads to balance the system, so it is not like they are using those extra conductors for just the one customer.We have many residential areas around me with only single phase running down the street.
But I do agree, this is not an issue in the OPs case.
We get that kind of thing around here when some electrician from a bigger city comes out here for a project - some seem really baffled at the concept of the high leg.I know of an apartment building near here that had a 240V 3P high leg service but when it was being built the electricians wired it as if it were 208/120, i.e., 1/3 of the units had the B (high leg) phase with the neutral from the A and C center tap. Oops.
If 3ph were not too far away theoretically you could run/bury a line specifically for a single customer with the common sresidential ervice drop being 120/240 where would 208y/120 be sourced? Unless the pri dist was 3p, such as 2300v, 4160v we here you could add a 3ph transformer it isn't going to happen. I would conceed that if money was no object it wouilkd not be an impossibility.The capacity of service he mentioned in post 8 isn't all that likely to just tap on to some already existing POCO secondary conductors, unless it is an existing building being renovated.
Why wouldn't there be three phase primary in a residential neighborhood? May not be present adjacent to each lot but chances are it isn't too far away.