We have 3ph overhead powerlines here in our neighborhood. I believe they are 4160-4400V. It's uncommon tho (aerial, anyway).
It would be interesting if you hcould see you transformer is fed from.
We have 3ph overhead powerlines here in our neighborhood. I believe they are 4160-4400V. It's uncommon tho (aerial, anyway).
It would be interesting if you hcould see you transformer is fed from.
Ill try to snap some pics tomorrow of the disconnects/transformer connections. The overhead lines are 3 wires up top, 1 a bit below, and cable/phone below that. Each pole has just one transformer, tho I imagine if I look closely, each one down the street is probably coming from a different phase.
May one of the lines be a ground to protect the lines from a lightning strike? If the transformer is fed from those line you would as lso think there should be a fused cutout switch that feeds the transformer. Is it a pole mount transformer or padmounted?
All of the transformers for residential in this area are pole mount. I dont think the switches from the overhead (3ph) to the transformers are fused; they look like a straight disconnect....
That disconnect you see has a fuse in it I'll bet.
Most all the single phase pole mounts around here have internal overcurrent device, and external operating handle. They do use external fuses on most three phase banks though. There is a lot of 240/480 single phase transformers for irrigation services - those usually do have an external fuse applied.All of the transformers for residential in this area are pole mount. I dont think the switches from the overhead (3ph) to the transformers are fused; they look like a straight disconnect. Keep in mind this neighborhood was built in the 50s. Newer construction has pad mound transformers and buried POCO lines. afaik, here, fusing for POCO mains is done fairly far away, maybe at the substations? I know Ive seen a fair share of blown transformers around here in storms; we lose power all of the time.
If 3ph were not too far away theoretically you could run/bury a line specifically for a single customer with the common sresidential ervice drop being 120/240 where would 208y/120 be sourced? Unless the pri dist was 3p, such as 2300v, 4160v we here you could add a 3ph transformer it isn't going to happen. I would conceed that if money was no object it wouilkd not be an impossibility.
With overhead service I haven't seen 3ph in a residential neighborhood. With underground service padmounts are 1ph.
With either s loop are radial feed primary I am not aware on any that feed 1ph trasnsformers.
It would be great if we got some input from someone we go in familiar with how a POCO distributes power.
That is common here in old buildings but not new ones.
Some do have a meter and still don't pay the bills (for various reasons) and little incentive to be conservative ...just saying.In most areas, a single meter for new construction would be a violation of adopted energy codes. People have no reason to conserve electricity if they aren't paying the bill.
151923-0055 EDT
Also on our block there is at least one home with three phase open delta service. On the block across the street from our block on a different primary feed there is at least one home with three phase service. i don't have three phase, but I could easily have it with the addition on one transformer.
I live in a humongous apartment building. It's served by 8 three phase padmount transformers, each around 2,000 kva. (Told you it was humongous). My apartment has a full three phase 208Y/120 service.
View attachment 13642
151923-0055 EDT
In my neighborhood we have a primary that is three phase delta. There is no overt neutral. At the substation it may very well be a wye with the neutral earthed.
Also on our block there is at least one home with three phase open delta service. On the block across the street from our block on a different primary feed there is at least one home with three phase service. i don't have three phase, but I could easily have it with the addition on one transformer.
Photos of my primary and transfomer are at http://beta-a2.com/misc_TMP_photos.html .
See photo P4 in particular.
.
I agree and it is not there to protect the transformer. It's there so if a transformer has a primary side fault it does not take out the over current device upstream.
No. If the fault is solid enough, enough fault current is available, and close enough to the transformer, the primary fuse will open.
No. Transformers will stand up to a good sized fault for a short period of time. If enough current develops to take out the fuse fast enough, the transformer will not be damaged.
I agree and it is not there to protect the transformer. It's there so if a transformer has a primary side fault it does not take out the over current device upstream.
2,000 sf, all electric.
View attachment 13742
Single phase panel would have done, but still, I like it That panel schedule is the most professional Ive seen for a dwelling, in fact most buildings.
Agreed on the panel schedule. When I worked for the poco, I saw a lot of new $400k+ homes with blank panel schedules, or incomplete and sloppily filled out schedules. I realize it's kind of a pita to take the time to fill one out neatly but it's part of the job. Reflects poorly on the electrician when it's blank or half-assed. IMO.