newservice
Senior Member
- Location
- Syracuse NY
- Occupation
- Electrician extraordinaire
Hi, I am a limited master license. Recently a customer had me look at a compressor he wanted to install at his car wash, to replace one he said had stopped working. On examination, he had a 415V, 3 phase motor not working but he didnt care, he wanted the new compressor installed so I did. The building was served by a single phase overhead drop from the pole which went to a 120/240v panel. Simple enough, and this is where I installed the compressor as the nameplate on the motor said single phase 240v and showed a line to line connection , no neutral.. All well and good.
Where it got interesting was looking at the 3 phase. The old motor was connected to only 2 of the phases, and one of them had a blown cartrige fuse in the 3 pole disconnect. When checking the voltages, I find 240 line to line on two of the wires and no other line voltages. Wheres the third phase? Seemingly worse yet, the line to ground (didnt have a neutral nearby to measure against so I went to the rigid pipe) ..was 240V for each of the two lines. Next I went back outside to look at the 3 phase drop, and it was only 2 line wires and a ground, just like the single phase! What gives? Im assuming the 3 phase is supposed to be a 240/416, so wheres the other wire from the pole transformer, and why is the line to line same as the line to ground? Am I missing something or is there a big problem? Given the massive size of these motors, I cant believe they would be made for just phase to phase connection and not a full 3 phases, but if they are, would the POCO supply only 2 wires of the 3 phase and this still doesnt explain the neutral to line being the same as line to line, unless, did they use the uninsulated neutral service drop conductor as the line and omit a neutral?
Didnt have a chance to pull the front from the panel as he would have had to shut down the car wash but thinking thats one of the next moves, because even if it is only 2 of 3 phases should still be 416V between them?
Thanks in advance for your thoughts.
Where it got interesting was looking at the 3 phase. The old motor was connected to only 2 of the phases, and one of them had a blown cartrige fuse in the 3 pole disconnect. When checking the voltages, I find 240 line to line on two of the wires and no other line voltages. Wheres the third phase? Seemingly worse yet, the line to ground (didnt have a neutral nearby to measure against so I went to the rigid pipe) ..was 240V for each of the two lines. Next I went back outside to look at the 3 phase drop, and it was only 2 line wires and a ground, just like the single phase! What gives? Im assuming the 3 phase is supposed to be a 240/416, so wheres the other wire from the pole transformer, and why is the line to line same as the line to ground? Am I missing something or is there a big problem? Given the massive size of these motors, I cant believe they would be made for just phase to phase connection and not a full 3 phases, but if they are, would the POCO supply only 2 wires of the 3 phase and this still doesnt explain the neutral to line being the same as line to line, unless, did they use the uninsulated neutral service drop conductor as the line and omit a neutral?
Didnt have a chance to pull the front from the panel as he would have had to shut down the car wash but thinking thats one of the next moves, because even if it is only 2 of 3 phases should still be 416V between them?
Thanks in advance for your thoughts.