I hope you mean wire them in parallel....View attachment 12622 The tech support for this steamer said changing this 3 phase 208v unit to single phase 240v is very complicated and that they could not provide a diagram. Shouldn't I be able to rewire the heating elements in series for single phase?
They want you to send it in to them so they can make $$$ converting it. It is not that hard. As mentioned put the individual elements in parallel across a 240 volt single phase input.View attachment 12622 The tech support for this steamer said changing this 3 phase 208v unit to single phase 240v is very complicated and that they could not provide a diagram. Shouldn't I be able to rewire the heating elements in series for single phase?
I mentioned some of this already and it seems to have components capable of handling more then what is connected - even if connected for single phase. Appears it has option of either a 35 or 60 amp mercury contactor a L15-30 cord cap and 30 amp circuit breaker according to the drawing posted and only a load of 3000 watts.First, to convert to 240V 1?, you should get the 240V heater elements. However, that is not all.. You have to change out the plug, cord, breaker, [most, if not all] internal power wiring, and likely the contactor [i.e. if it's only rated for three phase current levels].
I mentioned some of this already and it seems to have components capable of handling more then what is connected - even if connected for single phase. Appears it has option of either a 35 or 60 amp mercury contactor a L15-30 cord cap and 30 amp circuit breaker according to the drawing posted and only a load of 3000 watts.
Unless I am misreading it - is possible there are three 3000 watt heaters in which case the 30 amp breaker is actually slightly undersized if considered a continuous load and using on 208 volts.
Eyesight correct. Each channel heater is 3kW, for a 9kW total.I took it as 3 x 3KW.
I blame it on my eyesight.
First, to convert to 240V 1?, you should get the 240V heater elements. However, that is not all.. You have to change out the plug, cord, breaker, [most, if not all] internal power wiring, and likely the contactor [i.e. if it's only rated for three phase current levels].
The control wiring before the CPT should actually see less after switching primary voltage tap. Everything on the low voltage side of the CPT will remain the same.There is no power run to the unit now and changing out the cord is a given. Wouldn't the controls see the same current draw, they are only using two hot legs? Also, I've forgotten how to determine what the new draw will be. Something to do with the square root of three, although it would be super easy to temp power it and put an amp probe on it.
If you replace the elements with the correct part number for the voltage, the current per element should be lower for the 240V model.The control wiring before the CPT should actually see less after switching primary voltage tap. Everything on the low voltage side of the CPT will remain the same.
As far as current draw, what does the nameplate say? Compare to current level for 208V in my last post. Should be slightly more. Take that difference and add to the amount for 240V 1?.
That's not what I'm saying in that post. I'm saying the nameplate current for the existing 208V model should be slightly higher than the current draw of just the 3x3kW heaters to account for control power draw... and the difference will be the same no matter how the heater elements are configured. So simply add that difference to the currrent draw of 3x3kW 240V elements wired in parallel for 1? operation (37.5A) for total draw.If you replace the elements with the correct part number for the voltage, the current per element should be lower for the 240V model.
It may very well be supported by the factory to convert to single phase. Would be a good reason why the schematic mentions both a 35 amp and a 60 amp contactor being possible.I think you should put aside the way you would do this for moment and look at should you do this.
No doubt this is a listed appliance and these modifications would be a violation of 110.3(B).
I would not modify this appliance for a customer without factory support.
Or it may be that support only factory selection of the configuration with no field modification possible and they just economized by providing one schematic that showed the parts but not the wiring for the 240 configuration?It may very well be supported by the factory to convert to single phase. Would be a good reason why the schematic mentions both a 35 amp and a 60 amp contactor being possible.
I kind of wondered when I was thinking the 60 amp contactor was probably what is needed if single phase - but if they are going to mention it then why not draw alternate wiring - plus it wouldn't need to be a three pole contactor.Or it may be that support only factory selection of the configuration with no field modification possible and they just economized by providing one schematic that showed the parts but not the wiring for the 240 configuration?
It may very well be supported by the factory to convert to single phase.
The tech support for this steamer said changing this 3 phase 208v unit to single phase 240v is very complicated and that they could not provide a diagram.
:thumbsup: If you would use only one pole.I kind of wondered when I was thinking the 60 amp contactor was probably what is needed if single phase - but if they are going to mention it then why not draw alternate wiring - plus it wouldn't need to be a three pole contactor.
They may not support it but it is not that complicated for any electrician that is used to hooking up or troubleshooting controls. Those that don't do much but bend pipe, pull conductors and connect simple devices and fixtures maybe have a harder time with it.That does not sound like the factory supports the idea. But maybe.
With the equipment I work with that can be configured for single or three phase the information needed to do so is included in the diagram.
Most recently (within the last month) it was a 10 KW unit heater.