That would work, but it will give you only 208 volts phase-phase. No, you can't simply add the two 120 volt components to get 240 because they are not in-phase with each other.it is a 120v/208y 3 phase 4 wire panel. cant i just take two legs of 120 and use them to create the 240? i guess that would make it a 2 phase. i still need a single phase!
Generally when someone says "3-phase, 4-wire", they're referring to 3 phases and 1 neutral, not the ground, because technically you could have a system without a "wire" ground that uses bonded conduit as a ground if needed. The number of wires refers to the quantity of (normally) current-carrying conductors, which includes the neutral but not the ground.I don't know if there are differences in terminology or not, but when I hear 3-phase, 4-wire, that means 3-hots and a ground. A 5-wire system would have the neutral.
Different parts of the electrical industry have different definitions, which is why I prefaced my first posting the way that I did.Generally when someone says "3-phase, 4-wire", they're referring to 3 phases and 1 neutral, not the ground....
On a single phase 3-wire circuit a buck-boost will also affect the L-N voltage.Use a buck/boost transformer. Not that expensives and easy to do.
Gus
I am a little confused by this Jim. If you install a 208:240 transformer on a 208 system, the L-L will be 240 and the L-N will be 120 from the center tap of the transformer. There will not be a phase angle between the lines and neutral.On a single phase 3-wire circuit a buck-boost will also affect the L-N voltage.
That is true for a 2-wire 208V to a 3-wire 240V transformer.I am a little confused by this Jim. If you install a 208:240 transformer on a 208 system, the L-L will be 240 and the L-N will be 120 from the center tap of the transformer. There will not be a phase angle between the lines and neutral.
It is not really my neck of the woods, but why would you connect the neutral on the line-side of a buck/boost? That just wouldn't make any electrical sense to me. Without the neutral on the line-side, you have just two electrical points, and there can be no phase angle between two points.That is true for a 2-wire 208V to a 3-wire 240V transformer.
My statement was for a buck-boost transformer.
A 208/120V system would be boosted to 240/138V.
A 120/240V would would be bucked to 104/208V.
But if you look at the recent thread on adding a panel to a detached garage, the specific distinction was that a 120/240 "3-wire" system was installed instead of a 120/240 "4-wire" system as required under code.But I don't think that means a 3-phase 3-wire system doesn't have an EGC. I'd say that generally a grounding conductor is assumed unless specifically excluded. Does anybody do it differently? Of course, it does get confusing when you have 12/2 NM (with grounding conductor, 3 conductors total) and 12/3 SO (which also has 3 conductors). That really bothered me early on.
If you are wiring per the NEC, you can never have a 2-wire to 3-wire center-tapped buck-boost fed from a wye system.It is not really my neck of the woods, but why would you connect the neutral on the line-side of a buck/boost? That just wouldn't make any electrical sense to me. Without the neutral on the line-side, you have just two electrical points, and there can be no phase angle between two points.
As long as your buck/boost is connected line-to-line on the line-side, then the 3 output points (L1, N, L2) will always be single-phase and in-phase (e.g. 120/240). Right?
Jim, if memory serves me this is your area of expertise, so please forgive me, but I cannot find anything in code that makes such a statement (Edit to add: requiring the line-side neutral connection). I also can't think of a single reason why code would want to make such an assertion. Could it be that you are referring to a 3-phase transformer connected to a wye system instead of this single-phase transformer?If you are wiring per the NEC, you can never have a 2-wire to 3-wire center-tapped buck-boost fed from a wye system.
I have a problem with the Delta diagram: it shows the high leg as if the 208v was a source (a secondary.) In my opinion, they should show sources where the dotted lines are, and a dotted line where the 208v source is.Here is a picture I use frequently for questions about system types.