Let me start by saying that I know little if anything about 3-phase. I wired a 3-phase rotary converter about a year ago and besides that I've never had any experience with it.
I have taken a job to re-wire a former 3-bay and office auto workshop that is quite old and has been vacant for a few years. This building currently has a 100 amp. 3-phase service. I started last week by having the poco energize the building so I go tell what I had. I went by yesterday and everything in the building is working.
The 4 wire feeder to the building consists of 3 #3 copper conductors for the three legs. The neutral is tied to #4 bare copper at the weatherhead. The ground is bonded to the neutral at the meter socket which is allowed here. From there it goes to a large fused knife type disconnect. Voltage readings line to neutral/ground read 120/120/240. From the disconnect there are 2 3-phase subpanels with their loads long removed. There is also a main lug only panel servicing the 120/240 loads which consist of about a half dozen 8' flours. lights, 2 gas furnaces/ no a/c, assorted 120 volt receps. and some outside lighting. The wiring, for the most part is run in emt.
The will be no permits or inspections required where this property is but I want a compliant and safe install.
My customer has just purchased this building to store and service his business trucks and is leaving it up to me to update. My plan so for is to replace the outside service and convert to a single phase since there is no current or anticipated need for 3-phase. I haven't decided yet weather to leave it at a 100 amp or upgrade to 200 till I meet again with the owner to discuss price of each.
I plan to use a similar design with the service in to a disconnect then about 12" over to the breaker panel.
Whats bothering me is that the current wiring consists of 2 1" emt conduits headed up from the panel and into the ceiling to all the lights and receps in the building. Each pipe consists of 6-8 conductors and a #4 bare as a shared neutral.
I would like to do this without pulling new wire but I doubt this is a compliant install. Can anyone shed some light on what I need to do with these circuits? Is this or has this ever been a compliant way?
Sorry for the long post.
I have taken a job to re-wire a former 3-bay and office auto workshop that is quite old and has been vacant for a few years. This building currently has a 100 amp. 3-phase service. I started last week by having the poco energize the building so I go tell what I had. I went by yesterday and everything in the building is working.
The 4 wire feeder to the building consists of 3 #3 copper conductors for the three legs. The neutral is tied to #4 bare copper at the weatherhead. The ground is bonded to the neutral at the meter socket which is allowed here. From there it goes to a large fused knife type disconnect. Voltage readings line to neutral/ground read 120/120/240. From the disconnect there are 2 3-phase subpanels with their loads long removed. There is also a main lug only panel servicing the 120/240 loads which consist of about a half dozen 8' flours. lights, 2 gas furnaces/ no a/c, assorted 120 volt receps. and some outside lighting. The wiring, for the most part is run in emt.
The will be no permits or inspections required where this property is but I want a compliant and safe install.
My customer has just purchased this building to store and service his business trucks and is leaving it up to me to update. My plan so for is to replace the outside service and convert to a single phase since there is no current or anticipated need for 3-phase. I haven't decided yet weather to leave it at a 100 amp or upgrade to 200 till I meet again with the owner to discuss price of each.
I plan to use a similar design with the service in to a disconnect then about 12" over to the breaker panel.
Whats bothering me is that the current wiring consists of 2 1" emt conduits headed up from the panel and into the ceiling to all the lights and receps in the building. Each pipe consists of 6-8 conductors and a #4 bare as a shared neutral.
I would like to do this without pulling new wire but I doubt this is a compliant install. Can anyone shed some light on what I need to do with these circuits? Is this or has this ever been a compliant way?
Sorry for the long post.