abrahamespinal9
- Dominican Republic
- Electrical Engineer
Greetings,
I have tried to find information about this issue that we have presented several time and still does not have a clear explanation. We tipically do SOLAR PV installations and in a lot of cases need to install a step down Dry type transformer in order to interconnect 480V (Delta) PV inverters to 208 Wye electrical systems. The problem that we face is that when we connect the neutral conductor between the existing distribution transformer and the new dry type transformer a high current >200A runs between the 2 transformers in the neutral conductor, even with no load. I have read some things about coupling impedance on parallel transformers, but really don't now what a practical solution for this cases could be. The result is that we have had in a couple of cases a burned neutral that have affected power lines on the same conduit and caused short circuit and damage.
A solution proposed have been to use a Delta 208V / Delta 480V transformer and avoid the neutral current, but truth is i don't know how a 208V Delta would behave connected to a Wye system.
Anyways i would like to understand why is this happening and what is the typical engineering solution to this.
If anyone have faced this or know a practical solution please let me know.
Best regards,
Best regards,