Jody Boehs
Member
- Location
- Fairview, Oklahoma, USA
- Occupation
- Controls and Electrical Manager
I have a new packaging machine coming to our plant. The spec sheet shows it is 400V 3ph. (odd voltage in my opinion) or 230V 3ph. if we get the standard version (still not sure what version they ordered). Our plant runs on 480V 3ph. wye.
Obviously I can transform from 480 to 230 but the transformer I was looking at is a Delta wired transformer. I understand the primary side is usually wired in Delta. The secondary side is also Delta wired. If I put 480V Wye into the primary side, Will this create a "high leg" on the secondary side since it is wired in Delta?
I've energized numerous transformers (that are wired in Delta on the primary side) with 480V Wye, but have never worked with a Delta wired secondary side.
The other option I have is if they got the 400V option, then I'll have to find a special order transformer to drop 480V to 400V.
Obviously I can transform from 480 to 230 but the transformer I was looking at is a Delta wired transformer. I understand the primary side is usually wired in Delta. The secondary side is also Delta wired. If I put 480V Wye into the primary side, Will this create a "high leg" on the secondary side since it is wired in Delta?
I've energized numerous transformers (that are wired in Delta on the primary side) with 480V Wye, but have never worked with a Delta wired secondary side.
The other option I have is if they got the 400V option, then I'll have to find a special order transformer to drop 480V to 400V.