3 phase voltage fluctuations with current spikes

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Are you say potentially an internal neutral issu? Open or loose

Exactly. Somewhere in your system you made a set of measurements where the L-N voltage was unstable. The utility made a measurement at the transformer and claims the L-N voltage is stable. You need to keep working your way 'upstream' (toward the transformer), checking L-N voltages as your L-N load changes at each point you have access to. When the L-N voltage switches from unstable to stable, you've gone past the weak link in the neutral.

-Jonathan
 