Computer rooms often feature Liebert type cooling systems. If that happens to be the case, you're certainly need 3-phase.
mdshunk said:Just won't be able to power any 3-phase loads.
Except for the fact that you've upsized due to voltage drop. Need to upsize that EGC too, which is where MC sometimes bites you.bob said:Your EGC conductor is based on the breaker size.
SE is the typical bare strands wrapped around the insulated conductors, while SER has a bare conductor paralleled with the insulated conductors, because there is an insulated neutral separate from the bare conductor. This is why MD called it "subfeed cable".ram11379 said:What is the difference between se and ser?
That depends on (a) the current load and (b) the acceptable voltage drop.Is #1 AL ok considering it is over 100' away?
That's for a reason, as MD also said.And no the existing wiring is in pipe and armored cable.
I can't imagine pulling aluminum anything through 160' of FMC.chris kennedy said:I would bid based on FMC and THHN.
Absolutely. I have a partial roll I found abandoned at a jobsite. Three blacks, one black with a white stripe, and a bare, all #2 al. It's perfect for 3-phase use.infinity said:He needs 5 conductors. Does they make SER with 5 conductors?
Again, depends on load and acceptable VD.ram11379 said:Ok as all the different options are coming in here... what wire size can we agree on considering the 160" run?
Yes, for 3-phase and beyond the main disconnect. The only way to eliminate the GEC is to use a wiring method that provides one.And am I correct in assuming I need 3 hots 1 neutral and 1 ground?
Absoloopy!infinity said:For my buck I would install a 3 phase feeder and panel. For 1 extra conductor you'll get a 50% increase in 120 volt circuit capacity.
You mentoned only line-to-neutral loads anyway, but keep in mind that, for each phase wire you eliminate, the larger the remaining one(s) must be to provide the same amount of power.ram11379 said:I honestly wasn't sure if I was going to run a 3 phase or single phase panel. I guess that is why I am here . If I go 3 wire w/g(single phase) I am limiting this panel to only 120 volt usage correct?
What will be your total load?Also still waiting on the opinions of WIRE SIZE.[/]
You're welcome. :smile:By the way thanks everyone for all the help.
LarryFine said:I have a partial roll I found abandoned at a jobsite. Three blacks, one black with a white stripe, and a bare, all #2 al. It's perfect for 3-phase use.
LarryFine said:I can't imagine pulling aluminum anything through 160' of FMC.
"Captain Kirk! I shall consider it!" ~ Bearded Spock in original Star Trek episode Mirror. Mirroriwire said:If you look close you will find a red stripe and a blue stripe as well as the white.
Since you mentioned "Mirror, Mirror," you should be aware that next week, on Monday, June 19 SciFi channel will be showing the Enterprise episodes that take place in the "alternate" universe -- complete with references to several eposides from the original series:LarryFine said:"Captain Kirk! I shall consider it!" ~ Bearded Spock in original Star Trek episode Mirror. Mirror
Thanx!kbsparky said:. . . next week, on Monday, June 19 SciFi channel will be showing the Enterprise episodes that take place in the "alternate" universe -- complete with references to several eposides from the original series:
Mirror, Mirror
The Tholian Web
Arena
A must see for any original Trek fan!