I don't know about that, I'm kind of partial to impedance grounded 480 Wye. Reliability (continuity of power) is high. Burns up a lot less equipment when things do fail. And I don't see any safety compromise.Originally posted by ray94553:
Modern engineeing practices have all but abandoned those configurations, favoring instead a grounded system.
Got one. Use it to chase the ground faults. The impedance is usually set to pull 5 amps(or so) on a grounded phase. One throws the switch on the pulser that shorts out part of the grounding resistor, and the current pulses from 5 to 10 amps. The pulsing current is a lot easier to see with the big clamp-on than a small steady current.Originally posted by ray94553:
Using a special clamp on ammeter with a hoop large enoug to open over the conduit the faulted circuit can be located. The ground current will only show on the conduit containing wires feeding the fault.
I am guessing this is a corner grounded delta secondary and that the primary is connected to the ungrounded Wye phase legs?Ray posted: One type of ground fault sensing device is a transformer with a grounded open delta secondary. No current will flow in the secondary until the ground circuit is complete, and the magnitude current will be limited to the resistance of the fault connection
Right! In the example below, there would be 240 volts driving high circulating current through the winding impedance, if the S leads of phases A and B were connected. (#7)Get one winding backward, then blooie!
Compare #2 and #4 in the sketch above. Connecting the two Finish leads (#2) begins a wye connection, giving a vector sum of 208 volts.But what if we reverse a wye winding
Originally posted by ronaldrc:
Rattus
Are you sure about that Rattus. Seems to me it would buck against the other winding and try to cancel the voltage out?
Reply: Ronald, that is what happens when the delta is wired right. Get one winding wrong, and you have 416V ready to wreak havoc.
But I still believe even with a delta you would buck and have uneven voltages?
Reply: Get it right, and your vector diagram is an equilateral triangle, all voltages equal. Get it wrong, and your vector diagram looks like a lightning bolt--appropriately so too.
Start and Finish. I got used to that in my motor re-winding days.the designation of F and S for the coil terminals.
Hi Rattus, I don't mind being zinged at all.Ed, I am going to zing you