Your line current is (14.0A)(sqrt3) = 24.25A, and (1.25)(24.25A) = 30.3A, so you are almost right, but you cannot round down that 0.3A. Your minimum fuse size is 35A.Do I need to divide by 1.732 in sizing the fuse in disconnect or not?
IQ7 Max. Continuous Current = 1.0 A
Total No. of Inverter = 42
1.0 x 42 x 1.25 = 52.5A = 60A Fuse
1.0 x 42 x 1.25 / 1.732 = 30.3 A = 30A Fuse
30A or 60A Fuse?
Thank You!
![]()
Your line current is (14.0A)(sqrt3) = 24.25A, and (1.25)(24.25A) = 30.3A, so you are almost right, but you cannot round down, so your fuse size is 35A.
Your line current is (14.0A)(sqrt3) = 24.25A, and (1.25)(24.25A) = 30.3A, so you are almost right, but you cannot round down that 0.3A. Your minimum fuse size is 35A.
You don't.Do I need to divide by 1.732 in sizing the fuse in disconnect or not?
You don't.
Current is just current.
You are correct, sir! Otherwise, my calculation is correct, but I didn't look up the inverter maximum current at 208V, which is what I assume his 3P voltage is. He stated it as 1.0A, which is what I used. BTW, you cannot use the module or inverter rating in Watts to set the rating of the OCPD; you must use the inverter Imax.I thought 220.5(B) allows you to round down to the nearest amp.
If you have a 3 phase system with (3) 2-wire loads/sources with power factor 1 connected in a delta as A-B, B-C, and C-A, and if each load/source has a current of 1 amp, then with two loads/sources connected to each line conductor, the current on A, B, or C will be 1.732 amps. Which applies to the OP.Forget the 1.732.
We are looking at currents here.
OK.If you have a 3 phase system with (3) 2-wire loads/sources with power factor 1 connected in a delta as A-B, B-C, and C-A, and if each load/source has a current of 1 amp, then with two loads/sources connected to each line conductor, the current on A, B, or C will be 1.732 amps. Which applies to the OP.
Cheers, Wayne
I have a hard copy of it. It's pretty good, and I've not been able to find it or anything comparable on line since SP went away.These inverters are connected in a 3ph delta configuration. So the current between the inverters and the inverter CB in the panel is just the inverter Imax and sizing the CB is Imax*1.25. But leaving the 3ph panel the currents combine into line currents using the 3ph rules. Since these are balanced it makes it easy, the line current out of the 3ph panel is the inverter Imax *SQRT(3). The size of the fuse in the disconnect is then Imax *SQRT(3)*1.25.
If the inverters were not balanced then things get tricky. There was an old SolarPro article that went into how to calculate the line currents in an unbalanced combination of inverters in a 3 phase system.
People can still download issues at solarprofessional.com. If you post the month and year of the article people can find it easier.I have a hard copy of it. It's pretty good, and I've not been able to find it or anything comparable on line since SP went away.
The hard copy I have doesn't have a publishing date on it. It was written by Marvin R Hamon, PE, if that helps.People can still download issues at solarprofessional.com. If you post the month and year of the article people can find it easier.
Dec/Jan 2010People can still download issues at solarprofessional.com. If you post the month and year of the article people can find it easier.