ive done alot of work on parking lot lighting, im still young though, and ive only ever seen 2 pole circuits. came across a store that had (4) 3 pole parking lot lighting circuits. each circuit fed (2) 4 headed poles. what is the purpose of that and how would you wire the pole up? ive never seen a 3 phase hid ballast. i was only there to move a circuit from one contactor to another, didnt even have time to open up a pole base or head. just curious, thanks.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Could be wired any number of ways, but basically you are spreading the load over all three phases. You have a total of 12 fixtures,., ideally you would have (4) wired to Phases A-B, (4) to B-c and (4) to A-C.
Basically with only 2 phases (208v) on a 20 amp circuit you have 4.1 kw available, where with all three phases 7.2 kw.
 

iwire

Moderator
Staff member
Location
Massachusetts
I agree with Augie and will add that doing it the way he describes saves wire.

It is also very common in large parking lots.
 