Re: 3 prongs configured with ground in 2 wire system?
[/QUOTE]Also make sure that when inspecting older homes that have BX type wiring method, The BX is not used as an equipment ground. This does not include the newer type of BX that has the flat grounding conductor run inside of it, this is legal for grounding, but the older stuff that will only have the current carrying conductors with no extra grounding conductor in it and is not allowed to be used as a ground. Very dangerous as if a ground fault was to occur the casing can heat up like a heating element and cause a fire. Many have changed out 2-prong receptacles with this type of BX and I find it all the time in older houses. A very common over look.
My inspector allowes the old type metel BX jacket to be used for the EGC. I told him about this quote. He wants to know if you can site the NEC section to back up your quote.
[/QUOTE]Also make sure that when inspecting older homes that have BX type wiring method, The BX is not used as an equipment ground. This does not include the newer type of BX that has the flat grounding conductor run inside of it, this is legal for grounding, but the older stuff that will only have the current carrying conductors with no extra grounding conductor in it and is not allowed to be used as a ground. Very dangerous as if a ground fault was to occur the casing can heat up like a heating element and cause a fire. Many have changed out 2-prong receptacles with this type of BX and I find it all the time in older houses. A very common over look.
My inspector allowes the old type metel BX jacket to be used for the EGC. I told him about this quote. He wants to know if you can site the NEC section to back up your quote.