I forgot about the 10' area around the hot tub that can't be within the over head conductor area.
Conductor are 3' horizontal from edge of water and 16' from water. ( was thinking directly above the water.
Seems like I am boned, I tried to claim there service conductors so out of NEC code but that did not fly and these were existing so I should of caught it.
I would have to increase the service mast 10 feet to accomplish that height. Since the hot tub brings water level up 5' from grade.
Cheapest bet if owner is cool would be refund all his money and have him build a roof over the whole area so its enclosed.
Dang it.
just looked what I charged I will probably have to refund and pay to have this done o well.