Lee Graves
Member
On a project we're working on, we have (3) temporary poles with feed thru lugs supplied by one service. The poles are ~200' apart. They're 1p 4w. Should each pole get its own ground rod?
The difficult part: We lost (1) hot leg between TP01 and TP02. We are planning to re-phase the neutral conductor and use it as the lost hot leg. We will then re-phase the grounding conductor and use it as the neutral. This means between TP01 and TP02 we will only have a 3W system.
1. When we get to TP02, should we drive a ground rod since there is no grounding conductor being supplied on the line side? (currently the only ground rods are driven at TP01)
2. Should we install a main bonding jumper at TP02?
Thanks for the input,
Lee Graves
The difficult part: We lost (1) hot leg between TP01 and TP02. We are planning to re-phase the neutral conductor and use it as the lost hot leg. We will then re-phase the grounding conductor and use it as the neutral. This means between TP01 and TP02 we will only have a 3W system.
1. When we get to TP02, should we drive a ground rod since there is no grounding conductor being supplied on the line side? (currently the only ground rods are driven at TP01)
2. Should we install a main bonding jumper at TP02?
Thanks for the input,
Lee Graves