georgestolz said:
I disagree, I think you're reading too much into it - but that's just my opinion.
Edit to add: If your view is correct, then 250.32 is explicitly permitting a 250.6 violation when the neutral is used as the "inter-structure bonding jumper."
George maybe I am but here?s my logic with Lee?s application.
He needs 120/240v 1ph circuitry brought to 3 different temp. power poles. At minimum a 3w circuit is required to function
A, B, & N, but there are a few questions that must be answered to determine his application.
Q1: Are these services or feeders?
A: Outside feeders (225 II specifically applies)
Q2: Is there more than one building or structure involved?
A: Yes 3 temp. power poles (
250-32 specifically applies including the definition of structure)
Q3: Is an electrode required at each pole?
A: Yes (
250-32 specifically applies)
The quantity of conductors needs to be determined as well, 3 are for sure - A, B, & N - meaning the real issue
is an equipment grounding conductor [EGC] needed or not? If it is needed its function will be to provide the ?Effective Ground-Fault Current Path? as described in 250-4(5), and if it is not needed the neutral will provide this as a duel function also returning current. In this light a few more questions must be answered.
Q4: Is the 4th conductor [EGC] required?
A.1:
NO, if these are services the grounded conductor [neutral] provides this as per 250-24, 250-28 & 250-142(A) that includes the qualification of
250-32(B) (if Lee meets this qualification he will be allowed to use a 3w feeder [not service]!
A.2:
YES, because these are in fact load-side feeders rather than services and the rule is explained in a few places like 250-25(5) (that includes FPN to see
250-32) & 250-142(B) (that specifically links it?s reasoning to
250-32(B), (BUT again if Lee meets this qualification in 32(B)(2) he will be allowed to use a 3w feeder. George I don?t know if you realize this but this is what you agreed to in your post #18)
In summary these circuits can function safely as 3 or 4 wire only as determined by the criteria of 250-32 (B) and these are multiple structures which is only addressed in 250-32. It is the NEC that places all the emphasis for this type of application on 250-32 not me. My opinion of 250-32 has always been to use 250-32(B)(1) primarily and (B)(2) rarely in order to eliminate current on EGC?s as well as objectionable current, meaning if in doubt install an EGC and do not bond the neutral. In fact I?d like to see EGC?s from the utility service transformers and they can bond!
Lee can actually qualify as a 3 or 4 wire circuit I don?t know where else to qualify this other than 250-32. He has a unique situation in that he has lost a phase conductor and wants to use a 3 wire circuit but only Lee can determine this through the criteria of
250-32(B)(2).
So my view/opinion of 250-32 is NOT explicitly permitting objectionable current but it is
extremely integral to qualify the need of an equipment grounding conductor as opposed to using the neutral in a duel purpose (3 or 4 wire circuit in Lee?s case)