Hoggedy
Member
- Location
- Gloucester,VA,USA
Update: after further inspection and with the help of engineering we found that the secondary load current on the transformer was way under rated for its purpose.
3- 5kva single phase transformers
So 5000v ÷ 120v load voltage = 41 amps of the necessary 100 amp per line needed.
We are going to reinstall a 45kva transformer.
This way it will be 15000v per line÷120v load voltage= 125 amp of secondary current. Giving us the necessary ampacity.
It also showed why our transformer feeding one of the phases caught fire, due to an improper amount of secondary current on the single phase transformers.
3- 5kva single phase transformers
So 5000v ÷ 120v load voltage = 41 amps of the necessary 100 amp per line needed.
We are going to reinstall a 45kva transformer.
This way it will be 15000v per line÷120v load voltage= 125 amp of secondary current. Giving us the necessary ampacity.
It also showed why our transformer feeding one of the phases caught fire, due to an improper amount of secondary current on the single phase transformers.
Dang details get in the way of getting things done.
Yes, as stated by others the single larger transformer would be better.
How long did this setup work? Years, months, or for a few minutes after the switch was thrown?