3-way 4-way
hoody32
norwalk, ct
I have two 4-way switches going to the same boxes. Feed on one side and switch leg on the end. I have run the first switches with 3/wire. Can I run the second set switches with just the travelers?
how would you get the neutral from the light to the feed?
I think you'll need to post a diagram or spell out more explicitly each box, what it contains, and what wire type you want to use between what pairs of boxes.
Cheers, Wayne
Box one has the feed and a 3/wire. Box two has
Cheers, Wayne
if I have a box with
Cheers, Wayne
i have a BX feed coming into a 3 gang box to feed three 4-way switches, being switched from three locations for a chandelier, and sconces, and recessed lights. my first 3-way, 4-way, 3-way is run with a 3/wire cable which includes my neutral for all three boxes and my travelers for the first switch. (At this point I’m confident there is a neutral at every switching location). My question is: can I run the next switch with just 2/wire cable that includes just my travelers?
My thinking is, I can use the neutral from the first 3/wire cable to connect all the switch leg neutrals. I was told that this would create an imbalance and degrade the BX sheath over time. I personally don’t see it being any different than connecting all the switch leg neutrals in a 5 gang box with single pole switches.
Cheers, Wayne
I thought I replied to your comment but something strange happened. Please take a quick look at the thread comments
Sorry, still not following your description. If you don't want to upload a diagram, how a description like this:
Box A has 14/2 supply, 14/3 to Box B, and a 3-way switch
Box B has 14/3 from Box A, 14/2 to the load, 14/3 to Box C, and a 4-way switch
Box C has 14/3 from Box B and a 3-way switch
Cheers, Wayne
Seems he's asking if he can send travellers and a neutral in one cable, then only travellers in the second cable, and share the one neutral
5 conductos in 2 cables
T+T+N
T+T
No, you will a single current carrying conductor in the sheath, IOWs, you will not have any cancelling of the EMF.
Cheers, Wayne
Thank you for the response. What is “IOW”?