Electromatic
Senior Member
- Location
- Virginia
- Occupation
- Master Electrician
Care to elaborate on extending the circuit to more switches? The obvious way to do that would cause the light to be off only when all the switches are in the same position, and on whenever any two switches are in different positions. Which is not the desired control scheme, that flipping any switch will toggle the light state.You could theoretically keep the circuit going, but it ends up violating parallel conductor rules.
Yes, that's obvious. As my response indicated, I was referring to adding more switches.You end up with unswitched hot and neutral after the second switch. You could put receptacles, etc. downstream without it being affected by the switches
As I did until I submitted a PI to change "electrically joined" to "directly joined," citing examples of switching arrangements, and the CMP responded (to paraphrase) that it wasn't necessary as "electrically joined" already means "directly joined."Though the 'center' conductor does terminate at the switches, it is still a path for current, so I would consider that electrically joined.
Which is best handled by just routing all the conductors through the light box.There is the issue of the hot and neutral taking separate pathways.
It does during LD, RU = ON.For any load downstream of the switches, yes the hot and neutral take separate paths, but not for the light itself.
Maybe i didn't read everything... is there 2 hots legs? wouldn't LD/RD = BANG?left switch=L, right switch=R, up=U, down=D
LU, RU = OFF
LD, RU = ON
LU, RD = ON
LD, RD = OFF
You end up with unswitched hot and neutral after the second switch. You could put receptacles, etc. downstream without it being affected by the switches. If both switches are down, both conductors between the switches will be sharing the current of whatever is downstream of the second switch. Though the 'center' conductor does terminate at the switches, it is still a path for current, so I would consider that electrically joined. Unless you're wiring 3-ways with 1/0 or larger, it seems to me to violate 310.10(H). [unless the lights are indicating instruments!]
Yes and no; the latter simply creates a parallel pathway for any downstream loads.Maybe i didn't read everything... is there 2 hots legs? wouldn't LD/RD = BANG?
D'oh!It does during LD, RU = ON.
Oy, i did miss it. I wasn't seeing the highlighted red line showing the hot wire. I saw two separate hots. thanks.Yes and no; the latter simply creates a parallel pathway for any downstream loads.
Believe this is not always the way. I have seen the power go to the luminare box then 14/2 cable from there to first three way then another 14/3 cable between the three way switches. Ends up that neither three way locations have a grounded conductor.Standard 3ways always end up with a nuetral you don't have to dead end them always but if for some reason you need to dead end some so long as it's the same circuit it will work for smart switching
That's how you get messed up nuetrals unless you're carefullBelieve this is not always the way. I have seen the power go to the luminare box then 14/2 cable from there to first three way then another 14/3 cable between the three way switches. Ends up that neither three way locations have a grounded conductor.
LOL. Don't have that future apprentice go near knob and tube wiring.I've done it but hate using a 14 2 for travelers incase it throws off a future apprentice.
I was tought side by side when learning about that wiring method. I plan to always continue that method of teaching while working whenever working with any obsolete wiring with an apprentice. I also was drawn out examples while working with my jmen and have continued to do the same with my apprentices.LOL. Don't have that future apprentice go near knob and tube wiring.
that is the general rule, then there is sub part (3) that follows for non ferrous wiring methods which nullifies the general rule if using NM cable.I believe it is a violation of 300.3(b) which says all circuit conductors have to be in the same cable
Though this might be good practice, I don't believe it violates NEC as long as non ferrous wiring methods are involved.230806-2135 EDT
In any circuit you wire there is a source wire and a return wire. These two wires must be in close physical proximity to each other, preferably less than an inch apart for low voltage and current. 120 V and 20 A are low voltage and current for this purpose. None of this current should flow anywhere else. This is to minimize stray magnetic fields that may interfere with sensitive equipment.
.
.
It's not in (3) it's in (B) at the end "unless otherwise permitted in in accordance with 300.3(B)(1) through (B)(4). Last time I checked three is between one and fourCan you tell us what you see in that section which would nullify the general rule? I don't see anything View attachment 2566946
So, what do you see in anything between 1 & 4 which negates the mandate? I just don't see any wording there to support the notion. What's there that otherwise permits it?it's in (B) at the end "unless otherwise permitted in in accordance with 300.3(B)(1) through (B)(4)